6.5   Alterations and Additions for Outdoor Lighting

The Standards apply to alterations and additions to outdoor lighting systems. In general, additions are the same as new construction such as the mandatory measures and compliance with lighting power density requirements. The application of the Standards to alterations depends on the scope of the proposed improvements. In general, alterations to existing outdoor lighting systems that for any lighting application that is regulated by the Standards, increase the connected lighting load or replace more than 50 percent of the luminaires shall meet the requirements.

Some or all mandatory measures may apply to altered components. The mandatory requirements include certification of any new lamps, ballasts and drivers that are installed if they are the type regulated by the Appliance Efficiency Regulations. Any new lighting controls must meet minimum performance requirements.

For alterations that do not increase connected lighting load, but do replace 10 percent or more and less than 50 percent of the luminaires in a lighting application 'listed in Table 140.7-A or 140.7-B, only the altered luminaires are required to meet the applicable controls requirements of Sections 130.0, 130.2, and 130.4. The entire system is not required to meet Section 140.7, and LPD calculations are not required for the affected luminaires.

For alterations that replace more than 50 percent of the luminaires in a lighting application 'listed in Table 140.7-A or 140.7-B, all of the lighting in that application shall meet the applicable controls requirements of Sections 130.0, 130.2, 130.4, and 140.7.

Alterations that increase the connected lighting load in a lighting application 'listed in Table 140.7-A or 140.7-B require that the entire system in the application zone meet all the applicable requirements of Sections 130.0, 130.2, 130.4, and 140.7.

Lighting alterations generally refers to replacing the entire luminaire. Simply replacing the lamps and ballasts in an existing luminaire is not considered a lighting alteration. Retrofitting luminaires with another technology does not count as an alteration as long as the connected lighting load does not increase and the luminaire housing remains intact. Replacing or installing new wiring represents a lighting alteration and a great opportunity to meet the applicable mandatory requirements.

6.5.1    Outdoor Lighting Additions and Alterations – Mandatory and Lighting Power Density Requirements

A.   Mandatory Requirements

Additions to existing outdoor lighting must meet all of the Standards mandatory measures for the added luminaires. The mandatory requirements include certification of any new lamps, light sources, ballasts and drivers that are installed if they are the type regulated by the Appliance Efficiency Regulations. Any new lighting controls must meet minimum performance requirements. 'In 'addition, control and circuiting requirements apply as follows:

•      Motion sensing for incandescent luminaires rated over 100 watts

•      BUG zonal lumen limits for luminaires rated greater than 150 watts

•      Automatic controls to turn lighting OFF when daylight is available

•      Separate circuiting and independently controlled from other electrical loads by an automatic scheduling control

•      Motion sensing devices for luminaires mounted below 24 feet above ground that automatically reducing the lighting power of each luminaire by at least 40 percent, but not greater than 80 percent, auto-ON functionality when the area becomes occupied and no more than 1,500 watts of lighting power shall be controlled together.

•      Outdoor Sales Frontage, Outdoor Sales Lot, and Outdoor Sales Canopies shall have a part-night control or motion sensors capable of automatically reducing lighting power by at least 40 percent but not exceeding 80 percent, along with auto-ON functionality.

•      Building Façade, Ornamental Hardscape, and Outdoor Dining shall have a part-night control or motion sensors capable of automatically reducing lighting power by at least 40 percent but not exceeding 80 percent, along with auto-ON functionality, or a centralized time-based zone lighting control capable of automatically reducing lighting power by 50 percent.

•      All lighting controls must meet the requirements of §110.9.

A.   Lighting Power Density Requirements

The outdoor lighting additions must also comply with lighting power allowances of §140.7, Standards Tables 140.7-A and 140.7-B. These requirements are the same as new construction discussed earlier in this Chapter.

 

Example 6-39 Requirements for Parking Lot Additions

Question

I am adding a new 20,000 ft² section to our parking lot. What are the outdoor lighting requirements for the new addition?

Answer

§141.0(a) 1 specifies that all additions to existing outdoor lighting systems must comply with prescriptive requirements of §110.0 through 130.5 and §140.2 through §140.9.

Example 6-40 BUG Requirements for Parking Lot Lighting Replacement

Question

We are replacing 20 percent of the existing 250 W luminaires in a parking lot. Does the BUG requirement apply to the new and existing luminaires?

Answer

New luminaires may be required to meet the Uplight and Glare lumen limits, but luminaires that are not being replaced are not required to be upgraded to meet the Uplight and Glare lumen limits. §141.0 (b) specifies that all altered components must meet applicable mandatory requirements, including Uplight and Glare lumen limits for replacements luminaires. Therefore, replacement luminaires that are greater than 150 W must meet the Uplight and Glare limits of the Standards, even if less than 50 percent of the luminaires on site are replaced.

However, there is an exception to §130.2(b) where replacement of existing pole mounted luminaires in hardscape areas meeting all of the following conditions are not required to comply with the Uplight and Glare lumen limits:

•              Where the existing luminaire does not meet the luminaire Uplight and Glare lumen limits in §130.2(b); and

•           Spacing between existing poles is greater than 6 times the mounting height of the existing luminaires; and

•           Where no additional poles are being added to the site; and

•           Where new wiring to the luminaires is not being installed; and

•           Provided that the connected lighting power wattage is not increased.

Example 6-41 Requirements for Retrofitting Existing Luminaires

Question

In a service station we are retrofitting all existing luminaires under the canopy with new lamps, ballasts, reflectors, and lenses, while leaving the luminaire housing intact. Does this trigger the alterations requirements for outdoor lighting?

 

 

Answer

No, §141.0(b)2J specify that alterations requirements are triggered when the luminaires are replaced in a given function area, which includes replacing the entire luminaire including the internal components and the housing. In this example, because the luminaires are being retrofitted with new components, the alterations requirements of the Standards are not triggered.

Example 6-42 Requirements for Replacing Existing Luminaires

Question

In a service station we are replacing more than 50 percent of under canopy luminaires. Does this trigger the alteration requirements for outdoor lighting? Do we need to bring non-canopy lighting such as hardscape lighting up to code as well?

Answer

§141.0(b)2J specifies that when more than 50 percent of luminaires are replaced in a given Lighting Application included in Standards Tables 140.7-A and 140.7-B, the alteration requirements apply. So, in this example, all of the under canopy luminaires must meet the requirements of §140.7. Hardscape and other outdoor Lighting Applications other than the canopy need not meet these requirements even if they are included in the permit along with the canopy lighting.

Example 6-43 Requirements for Adding New Luminaires in a Parking Lot

Question

We are adding new luminaires to the existing lighting systems in a parking lot. Which Standards requirements are triggered by this alteration?

Answer

Because additional load is being added to the parking lot, which is part of the general hardscape lighting, the entire general hardscape area must comply with the lighting power density requirements for the given Lighting Zone. However, only the newly installed lighting system must comply with the applicable mandatory requirements, including control requirements and Uplight and Glare lumen limits.

Example 6-44 Requirements for Replacing Ballasts

Question

I am going to change the ballasts in my façade lighting system. Will I be required to meet the new Outdoor Lighting Standards for façade lighting?

Answer

No, the replacement of only lamps or ballasts in outdoor lighting systems is not considered an alteration and does not trigger compliance with Outdoor Lighting Standards. Replacing entire luminaires will trigger mandatory requirements for the altered (replaced) luminaires only. Replacing more than 10 percent of the luminaires or adding to the connected lighting load for any outdoor lighting application will trigger the lighting power density requirements of the Standards.

Example 6-45 Requirements for LED Retrofits

Question

I am going to retrofit all of my HID parking lot lights with an LED retrofit kit. What requirements do I need to follow for the LED retrofits?

Answer

As long as the LED retrofits do not increase the connected lighting load and the luminaire housing remains intact, there are no requirements for the LED retrofits.

6.5.2    Outdoor Lighting Alterations – Adding Outdoor Lighting to Existing Sites

In many cases, the general lighting for a site will be designed for a shopping center or a strip mall and stores or restaurants may be added later with additional lighting needs. In general, if one has a new outdoor lighting application (more doors, outdoor dining, retail sales) one can add the amount of lighting associated with the additional lighting allowances for specific applications contained in Standards Table 140.7-B. If this amount of lighting allowance is not enough, one can either re-design the proposed lighting system or re-calculate the hardscape lighting allowances for the entire site to identify if savings somewhere else on site can be used to add light for this application.

Outdoor lighting power allowances are based upon a "layering" of specific application allowances on top of general hardscape allowances. The general hardscape allowance has three components: the initial wattage allowance (IWA) which is available once per site, the linear wattage allowance (LWA) which is available for the perimeter of the hardscape and the area wattage allowance (AWA) which is available for the field of the illuminated hardscape area. For an outdoor lighting alteration, the LWA shall be applied only to the perimeter of altered portions of the site hardscape.  When the outdoor lighting is designed all at the same time, the outdoor lighting allowance is calculated as described in Section 6.4.5 of this chapter.

 

Example 6-46 Power Allowance for Additional Outdoor Dining (Inside Illuminated Area)

Question

A strip mall in Lighting Zone 3 with a common parking lot has its lighting system already designed and installed. A restaurant moves into one of the buildings and designates 400 ft² as outdoor dining. The outdoor dining area is within the illuminated area (5 mounting heights) of the pre-existing lighting. How is the allowable lighting calculated?

Answer

The allowable lighting power can be calculated in two ways:

Method 1

Calculate only the additional allowance layer for the outdoor dining area for specific applications (Outdoor Dining) as contained in Table 140.7-B of the Standards. In this case the allowance is 0.240 W/ft². Multiplying this allowance by 400 ft² yields 96 W.

Type of Allowance

Allowance

Area/Perimeter Value

Power Allowance

Outdoor Dining

0.240 W/ft2

400 ft2

96 W

TOTAL POWER ALLOWANCE

96 W

 

Method 2

One could have the permit cover all of the site lighting including the outdoor dining area. (This second compliance path would provide a greater power allowance, but would require more work in the application process.) This only yields a higher allowance if the current lighting system serving hardscape areas for the rest of the site has less wattage than the calculated total site hardscape wattage allowance. Additional allowances would be possible if one upgraded to the current hardscape system for other parts of the site and reduced its wattage.

Example 6-47 Power Allowance for Additional Outdoor Dining (Outside Illuminated Area)

Question

A strip mall in Lighting Zone 3 with a common parking lot has the parking lot lighting system designed and installed. A restaurant moves into one of the buildings and designates 400 ft² as outdoor dining. The outdoor dining area is outside of the illuminated area of the pre-existing parking lot lighting. How is the allowable lighting calculated?

Answer

'In 'addition to adding outdoor dining area, which is a specific application that is allowed more light, the illuminated general hardscape lighting area is also increasing in size by 400 ft². Adding illuminated hardscape area results in increased general hardscape area wattage allowances (AWA) and increased linear wattage allowances (LWA) but it does NOT add an additional initial wattage allowance (IWA) because only one initial wattage allowance is allowed per site. The allowable lighting power can be calculated in two ways:

Method 1

Calculate the general hardscape area wattage allowances (AWA) and the increase to the general hardscape linear wattage allowances (LWA) and the additional allowance layer for the outdoor dining area for specific applications (Outdoor Dining) as contained in Table 140.7-B of the Standards. As discussed above, it is not permissible to also claim the general hardscape initial wattage allowance (IWA) as this is calculated only once per site. The linear wattage allowance applies only to the new perimeter length, which is not adjacent to previously illuminated area that is part of the site.

As shown in the figure below, the perimeter length is 41 ft (25 ft + 16 ft). In LZ 3 the AWA is 0.090 W/ft² and the LWA is 0.60 W/ft. The additional allowance for the outdoor dining area for specific applications (Outdoor Dining) as contained in Table 140.7-B is 0.240 W/ft². Thus for a perimeter length of 41 ft and an area of 400 ft², the total lighting wattage allowance is:

Hardscape LWA of 0.60 W/ft x 41 ft = 25 W

Hardscape AWA of 0.090 W/ft² x 400 ft² = 36 W

Specific Allowance Outdoor Dining 0.240 W/ft². x 400 ft² = 96 W

                                                            Total allowance = 157 W

Type of Allowance

Allowance

Area/Perimeter Value

Power Allowance

Outdoor Dining

A.        0.240 W/ft2

B.        400 ft2

96 W

Area

0.090 W/ft2

400 ft2

36 W

Perimeter

0.60 W/LF

41 ft

25 W

TOTAL POWER ALLOWANCE

157 W

 

Method 2

One could have the permit cover all of the site lighting including the outdoor dining area. (This second compliance path would provide a greater power allowance, but would require more work in the application process.) This only yields a higher allowance if the current lighting system serving hardscape areas for the rest of the site has less wattage than the calculated total site hardscape wattage allowance.

Example 6-48 Power Allowance for Outdoor Dining

Question

A restaurant moves in next door to a strip mall and the strip mall has its own parking lot lighting. Although the restaurant is adjacent to the outdoor parking lot lighting of the mall, this restaurant has its own parking lot and is not on the same site as the mall. The restaurant is adding 400 ft² of outdoor dining. How is the outdoor lighting allowance calculated?

Answer

This restaurant is on its own site and is able to take the all of the general hardscape lighting power allowances (IWA, LWA, and AWA). This lighting system is also allowed to take the additional specific application wattage allowance for the 400 ft² of outdoor dining.